Inovance 10-2 fault code meaning
Inovance / 10-2
Series: MD580
Cycle-by-cycle current limiting fault
AC drive
Meaning: Fault category: drive overload; Default level: coast stop; Reset method: manual reset
Possible causes
- Acceleration/deceleration time settings too short
- Selected drive is undersized
- Sudden load application during operation
- Starting directly while the motor is rotating
- Short circuit at the output
- The load is too large or the motor has a locked rotor.
- Low DC bus voltage
- Other causes
Source: Inovance Official Function Manual 19011555 A00 P450
Series: MD580S, MD880
Cycle-by-cycle current limiting fault
AC drive
Meaning:
Possible causes
- Acceleration/deceleration time settings too short
- Selected drive is undersized
- Sudden load application during operation
- Starting directly while the motor is rotating
- Short circuit at the output
- The load is too large or the motor has a locked rotor.
- Low DC bus voltage
- Other causes
Source: MD580S Series Low-Voltage High-Performance Engineering AC Drive Function Manual P421; MD880 Series AC Drive Function Manual (HCU) P603